avmWhen a 3 phase system is balanced, what will be the current in the neutral wire ?
-
Member • Jan 7, 2009
Practically there is no balanced 3 phase system. Ideally in 3 phase balanced system neutral current will be "ZERO".
regards,Are you sure? This action cannot be undone. -
Member • Jan 8, 2009
I was also of your opinion. But i have seen in a book that the neutral current in a three phase balanced system is one third of the phase current. that is why i posed the question.
thank you for replyAre you sure? This action cannot be undone. -
Member • Jan 8, 2009
This case is for Star connection & delta connection when Line current & Phase current come into picture.
Check for phase current & Line current details. Your doubt will be resolved.Are you sure? This action cannot be undone. -
Member • Jan 8, 2009
first of all nuetral point is a null point,though it not an ground ,well theoritacally it should be ZERO,but practically its not possible so watever network you are considering you should try to keep it close to zero.Are you sure? This action cannot be undone. -
Member • Jan 8, 2009
Ideally, the current in the neutral wire is ZEROAre you sure? This action cannot be undone. -
Member • Jan 11, 2009
what are your views AVM. Did you find the answer to your querry?Are you sure? This action cannot be undone. -
Member • Jan 12, 2009
Thank u all who have contributed to the discussion...............................Are you sure? This action cannot be undone. -
Member • Jan 13, 2009
Neutral carries sum of three currents.
In a 3 ph system currents whose magnitude and angle are
1. I (0)
2. I (120)
3. I (240)
if we add all three we get zero..Are you sure? This action cannot be undone. -
Member • Mar 30, 2010
Neutral is the point at which all the three phase’s current meets and the algebraic sum of current becomes zero in case of “Balanced Load Condition”.
I = I1 + I2 + I3 = 0
When ALL phase has balanced load, neutral should be ZERO volt in respect to earth. Be careful the word “Balanced”, which means, if there is an unbalanced phased (due to load), the neutral will no longer be ZERO volt in respect to earth. When there is more than ZERO volt between neutral and earth, then there will be current flow through these 2 points (Leakage Current).
Even for most of the time, neutral and earth has ZERO volt between them; they should never be connected together or be used interchangeably.
Neutral: Return path of current flow in order to make a closed circuit [Return Path Conductor].
Earth: Path for Leakage current [Short Circuit / Fault Current / Crack in Insulation] in the circuit to protect Human & Equipment Safety.Are you sure? This action cannot be undone. -
Member • Mar 31, 2010
zero and there is no need for a neutral wire if it is truly balanced. The neutral wire keeps voltage spikes from occurring in an unbalanced system. It is unlikely that you will find a balanced system in the real world.Are you sure? This action cannot be undone. -
Member • Apr 3, 2010
nutral is only in star connection no nutral wire in delta am right?Are you sure? This action cannot be undone. -
Member • Apr 6, 2010
I [FONT="]though Ineutral = I1 + I2 + I3. and not zero. should have current as neutral are return path of the phase current right? [/FONT]Are you sure? This action cannot be undone. -
Member • Apr 7, 2010
theoretically it will be 0 but practically it will show readings close to 0 as there might be some lossesAre you sure? This action cannot be undone. -
Member • May 30, 2010
Why excessive neutral current dot desirable in power distribution systems?Are you sure? This action cannot be undone. -
Member • Aug 7, 2011
If 2 currents on phase A and B are 16 A and phase C is 10 A what is the current on the neutral? Thanks in advance for your help.Are you sure? This action cannot be undone. -
Member • Aug 8, 2011
i think it may be 4 or 8debskolmodinIf 2 currents on phase A and B are 16 A and phase C is 10 A what is the current on the neutral? Thanks in advance for your help.
because difference current flows in neutral to balanceAre you sure? This action cannot be undone. -
Member • Aug 13, 2011
do the phasor sum of current not scalarAre you sure? This action cannot be undone. -
Member • Aug 28, 2011
i think yes is the answerArpdo the phasor sum of current not scalar
as per my knowledge current lags voltage depending on load and each phase voltage is divided by 120 deg so current will be on same to the voltage
but it does not same for all the voltages as type of load change in phases the angle is also changes respective to the voltages
so there is some change in phase currentsAre you sure? This action cannot be undone.