Ok fellas
Ir. Rhett Kelly is a professional electrical engineer and the Chief Engineer of a leading power utility supplier. In case some of you do not know; Chief Engineer is the highest job title for any engineer in any discipline.
He responds as follows:
=======================================
The question is unclear and non specific.
A brief summary of issues to consider for cable conductor size determination (from an electrical perspective):
(note as this is intended for students in a foreign country, answers are not provided, but rather the questions/issues to consider)
1. required load (in MVA or Amperes) and load profile (i.e. load factor)
2. prospective short circuit current (symmetrical and earth fault) and duration (typically 1 second). The duration is determined, in general, by the protection settings applied and type of protection functions.
3. allowable voltage drop (where applicable)
4. technical losses (IxIxR) associated with a particular conductor size over a 25 year (typical) period brought back to net present value (often warranting a larger conductor / cable size than the load and system requires).
5. planned spare capacity for emergency/contingency scenarios
To determine the current ratings of insulated cables, refer to IEC 60287 (for 100% load factor) and IEC 60853 (for cyclic rating factors) for detailed equations or consult manufacturers catalogues. The short circuit ratings of cables can be calculated assuming adiabatic conditions using equations based on the initial and final conductor temperatures, the conductor material, the conductor cross section and the short-circuit duration (typically 1 sec).
The current rating of a cable is affected by the following:
1. the maximum continuous conductor temperature allowed - this depends on the insulation material
2. the maximum short circuit conductor temperature allowed - this also depends on the insulation material
3. the installation conditions - namely:
-free-air above ground vs directly buried underground cable vs cable installation in pipe ducts vs cable installation in air within ventilated tunnels)
-ambient air temperature (annual average) for installations in air
-soil temperature (annual average) for direct buried cables or cables in pipe ducts in the ground
-spacing between cables and/or other circuits (i.e. presence of external thermal sources in proximity) for direct buried cables
-depth of burial for direct buried cables
-soil thermal resistivity for direct buried cables
-for single core cables - the configuration (flat vs trefoil formation)
-for single core cables - the type/method of earthing applied to earth the cable metallic screen/sheath (also referred to as special bonding to limit / eliminate sheath circulating currents)
Regards,
Rhett Kelly Pr. Eng.
Chief Engineer - Technology Development
Power Plant Technologies
Eskom Corporate Services
Johannesburg, South Africa
#-Link-Snipped-#
=======================================
Please note that Ir. Kelly echoes my gripe
viz.
The question is unclear and non specific.
PS a BIG thanks also to Dr. Mark van der Riet