Why does a motor take 1 ampere when current passes through auxiliary contacts, whereas it takes 10 ampere?

Kumar Sahoo

Kumar Sahoo

@kumar-JBoFlF Oct 26, 2024

motor takes 1 ampere when current passes through auxiliary contacts it takes 10 ampere why?

Replies

Welcome, guest

Join CrazyEngineers to reply, ask questions, and participate in conversations.

CrazyEngineers powered by Jatra Community Platform

  • Ramani Aswath

    Ramani Aswath

    @ramani-VR4O43 May 9, 2019

    The question is not clear. A sketch of the circuit may help.


  • Kumar Sahoo

    Kumar Sahoo

    @kumar-JBoFlF May 10, 2019

    A single phase  1 HP motor connected  with a DOL starter which  having  2 push buttons one is start(green) another one is stop (red). As per the  principle  of W= √3VIcosΦ the motor should take 1.48amps but it's taking  10 Amp.  How? 


  • Ramani Aswath

    Ramani Aswath

    @ramani-VR4O43 May 10, 2019

    In a single phase motor, W= VxIx cos(phi).

    Full load current of a 1 hp induction motor will be about 8 amps taking into account power factor.

    You seem to be taking the formula for the single phase current of a 1 hp three phase induction motor.

    Please see here:

    <a href="https://www.engineeringtoolbox.com/elctrical-motor-full-load-current-d_1499.html" target="_blank" rel="nofollow noopener noreferrer">Electrical Motors - Full Load Amps</a>