  • Why we use 4-20mA current signals instead of voltage?

    Updated: Oct 26, 2024
    Views: 1.3K
    This video has answered this question:



    this question has always made me wonder, but now I got the answer. If you have other points more than the ones mentioned, please contribute.

    Best regards!
    0
    Replies
Howdy guest!
Dear guest, you must be logged-in to participate on CrazyEngineers. We would love to have you as a member of our community. Consider creating an account or login.
Replies
  • Carl Ellis

    MemberJul 2, 2017

    THE Number One reason for using 4-20mA current signal is for loop powered instrumentation requiring only 2 conductors/wires from the 'control room' receiver to the field. The minimum 4mA value allows 3.5mA or 3.6mA to be used to power the instrument, without additional power conductors.

    The other cited reasons are indeed advantages of a current loop over voltage, but are not the main reason 4-20mA has such widespread acceptance and useage; the main reason is loop power functionality.
    Are you sure? This action cannot be undone.
    Cancel
  • Piyush Yadav

    MemberOct 9, 2017

    Excellent explanation with in the video but i know about 4-20mA Loop powered sensors, those are mostly used for Vibration measurement for process control system...as there are many variation in instrumentation and their features that's why i uploaded a picture, you may recognise them...
    Are you sure? This action cannot be undone.
    Cancel
  • Nate Pulkar

    MemberApr 5, 2018

    What is the difference between 4-20 Current Receivers and 4-20 Current loop Receivers and which is much better for industrial standards
    Are you sure? This action cannot be undone.
    Cancel