VCB vs SF6 CB

er.satish

er.satish

@ersatish-qMIyMx Oct 26, 2024

pls give us difference between Vaccum Circuit breaker and SF6 CB, which is more reliable, better in operation and cost effective ?

Replies

Welcome, guest

Join CrazyEngineers to reply, ask questions, and participate in conversations.

CrazyEngineers powered by Jatra Community Platform

  • d_vipul

    d_vipul

    @d-vipul-wP6Syg Sep 10, 2010

    In VCB, breaker contacts are placed in VACUUM. In vacuum arc easily extinguished as their is no medium for arc to survive.
    It is good for voltages below 33kV.

    In SF6 CB, the contacts are placed in a vessel containing SF6 gas. When the contacts are allowed to open SF6 gas it allowed to pass over through contact gap and contacts.
    It is mostly used for voltages above 66kV.

    Both are reliable, good in operation and good electrical properties but SF6 CB are costlier than VCB.
    But the technology used for VCB for production is much costlier than SF6.

    SF6 needs more maintenance than VCB.
    VCB unit is changed directly when it is warned out with the new one.

    Hope this is satisfies your need.
    If you have more doubts then feel free to ask me.
    I will answer to it in 24 hours.

    Regards,
    VIPUL