Temperature Control In Air Coolers - Possible? Ideas?
Let the electric pulses flow through your brain and come up with an idea to fix this problem.
Member • Mar 19, 2014
Member • Mar 19, 2014
Administrator • Mar 21, 2014
Member • Mar 21, 2014
Administrator • Mar 21, 2014
Member • Mar 21, 2014
Member • May 24, 2017
You must be familiar with cooling tower design which works on the same principle of evaporative cooling.There are two variables namely air flow rate and water flow rate which are determined to arrive at the desired wet bulb temperature.It is possible to vary both the variables through fan speed and water pumping rate.However,we seldom get to the exact wet bulb temperature due to efficiency losses.Similarly, it is possible and sometimes necessary to control the outlet temperature in a air cooler say in a place like Hyderabad where the dry bulb temp in peak summer is around 44 deg C and RH as low as 8%.This gives you a wet bulb temp of around 16 deg C,which is far lower than the comfort temperature of 24 deg C to 26 deg C.We can achieve comfort temperature by lowering the fan speed,and most models come with 2-3 fan speed settings.The water pumps in most models come with fixed speeds and pumping rates,and hence not possible to vary the flow rates, though theoretically possible to vary them with VFDs.Kaustubh KatdareI'm specifically interested in finding out whether we can control the temperature of the air blown by the air-cooler.
How about regulating the flow of water? Can that help?