    With an Amara Raja Amaron Tribal UPS/Inverter 1400va/24v and with a connected load of 365 watts I need a back up for 4 hours. I have 2X12 V 150ah batteries. Do you think I can run one 32 inch LED TV, one desktop PC, 2 LED lightsX23 W and 2 fans? I am getting alarm signal indicating low battery after half hour. Is it the fault of the inverter I purchased one month back or some thing else.
    0
    Replies
Howdy guest!
Dear guest, you must be logged-in to participate on CrazyEngineers. We would love to have you as a member of our community. Consider creating an account or login.
Replies
  • Safo Kofi

    MemberDec 11, 2016

    Ravi7640
    With an Amara Raja Amaron Tribal UPS/Inverter 1400va/24v and with a connected load of 365 watts I need a back up for 4 hours. I have 2X12 V 150ah batteries. Do you think I can run one 32 inch LED TV, one desktop PC, 2 LED lightsX23 W and 2 fans? I am getting alarm signal indicating low battery after half hour. Is it the fault of the inverter I purchased one month back or some thing else.
    What are the sum voltage of the overall equipment......
    Are you sure? This action cannot be undone.
    Cancel
  • Duppa

    MemberDec 11, 2016

    Safo Kofi
    What are the sum voltage of the overall equipment......
    Lets us assume that desktop computer (CPU) takes 100 Watt. The monitor takes 40. Two fans = 50 Watt *2 = 100 watt. 32 Inch TV = 55 Watt
    The sum = 100 + 40 + 46 + 55 + 100 = 341 watt.
    Everything runs on a 230 Volt Phase to neutral voltage.
    Are you sure? This action cannot be undone.
    Cancel
  • Safo Kofi

    MemberDec 11, 2016

    Duppa
    Lets us assume that desktop computer (CPU) takes 100 Watt. The monitor takes 40. Two fans = 50 Watt *2 = 100 watt. 32 Inch TV = 55 Watt
    The sum = 100 + 40 + 46 + 55 + 100 = 341 watt.
    Everything runs on a 230 Volt Phase to neutral voltage.
    Well I don't believe the fault is that of the inverter....th inverter only convert the dc voltage from the a source maybe a solar panel or something else to Ac...the problem is the battery....try replacing them and let's see the result...pal
    Are you sure? This action cannot be undone.
    Cancel
  • Ravi7640

    MemberDec 11, 2016

    Well, I wouldn't think so. The 2 batteries of Amaron was purchased along with the inverter 1 month back and is perfectly healthy. I had attached a Phocos solar priority controller system which connects my PV panel along with the grid power to the system.