No load losses of the transformer

aarthivg

aarthivg

@aarthivg-HH344f Oct 22, 2024
How the no load losses of the transformer can be minimized ?

Replies

Welcome, guest

Join CrazyEngineers to reply, ask questions, and participate in conversations.

CrazyEngineers powered by Jatra Community Platform

  • Ramani Aswath

    Ramani Aswath

    @ramani-VR4O43 Mar 27, 2012

    If you use superconducting coils, the efficiency will be of the order of 99.85%.
  • Harshad Italiya

    Harshad Italiya

    @harshad-ukH5ww Mar 27, 2012

    bioramani
    If you use superconducting coils, the efficiency will be of the order of 99.85%.
    And remaining 0.15% are because of the core we are using in transformer? I am not sure.
  • Shreyas Sule

    Shreyas Sule

    @shreyas-yx6FwP Mar 27, 2012

    The no load losses are due to:
    1. Hysteresis- In core laminations
    2. Eddy current-In core laminations
    3. Stray Eddy current- In core clamps, bolts and other components
    4. Dielectric losses.
    5. I2R losses-Due to no load current
    Hysteresis losses and eddy current losses are the primary contributers (about 99%) of the no load losses.
    Eddy current losses are reduced by using thinner and better quality of core steel and designing the core effeciently. Hysteresis losses are caused by molecules in the core laminations which resist getting magnetized and demagnetized by the alternating magnetic field. This resistance by molecules causes friction and heat is generated. Hystersis losses can be reduced by selection of proper size and type of core material.