How to know the VA rating of a transformer

Hello to all


I am an electrical engineer and in an interview I was asked to tell the MVA rating of a transformer of few KV , and nothing was given means neither the power factor and nor the current , so I want to ask you people is there any way to determine the MVA rating of the transformer from the KV or vice-versa.


Please tell me with an example if possible.



Thank you

Replies

  • u_know_who
    u_know_who
    As far as i am concerned in XFR (transformer) both KV and MVA rating are mentioned. Both of them are essential because you can calculate rated current, rated impedence etc from this two value. So KV and MVA rating are independent variable. I don't know if there is practical function between them.

    May be in practice there is some combination of this two. Which requires practical knowledge not mathematical issue.
  • Arp
    Arp
    not possible to tell the exact VA rating of the transformer given.
    but if given the Voltage then u can decide whether it is coming inthe distribution or transmission or which range. then u can give an approx estimation of the KVA rating. ok
  • piyushpandey
    piyushpandey
    Arp
    not possible to tell the exact VA rating of the transformer given.
    but if given the Voltage then u can decide whether it is coming inthe distribution or transmission or which range. then u can give an approx estimation of the KVA rating. ok
    hello arp

    first of all thanks for your reply .

    Actually I meant the same that how can you estimate the approximate value of the VA as ofcourse it is impossible to get the exact value of VA from the value of just of voltage and not the current.

    So can you show this with an example, please.



    Piyush Pandey
  • Arp
    Arp
    As an example, if the voltage rating of two sides are like 11 kv and 220 kv indicates it is a generating transformer so its rating is someewhat in range- 100to 200 MVA, if 15.75 kv then 300 MVA and if 21 kv to 220 kv then can be 600-900 MVA even.
    if rating are 11 kv and 33 kv indicate its rating around 20 MVA.
    if unit auxillary transformer (6.6/433) then should be around 2-4 MVA
    if distribution one then should be around 25KVA to 10 MVA usually 1-10 MVA.
    data taken from my internships done
    if any furthur query u have, post here.
  • Alienator
    Alienator
    Arp
    As an example, if the voltage rating of two sides are like 11 kv and 220 kv indicates it is a generating transformer so its rating is someewhat in range- 100to 200 MVA, if 15.75 kv then 300 MVA and if 21 kv to 220 kv then can be 600-900 MVA even.
    if rating are 11 kv and 33 kv indicate its rating around 20 MVA.
    if unit auxillary transformer (6.6/433) then should be around 2-4 MVA
    if distribution one then should be around 25KVA to 10 MVA usually 1-10 MVA.
    data taken from my internships done
    if any furthur query u have, post here.
    whats the math behind it? bro...
  • Arp
    Arp
    no math behind it just logic
    what i know is the line voltage rating of the different rating alternators. from there u can know the kva rating of transformer if know the line voltage.

You are reading an archived discussion.

Related Posts

Need some suggestion for project topics
Assume that a 2400 foot magnetic tape has recording density of 6400 Bpi. Data (logical) records are 100 bytes, and the memory buffer is 10,000 bytes. What is the largest...
Here are some PHP books for referemce-Please suggest which of them are good. Also please post any other if you know - O'Reilly-php cookbook Apress beginning php and mysql 3rd...
Could any one tell us which books are good for Java developers.. I have list of few books. Help me in knowing which is good : 1.Thinking in JAVA -...
Richter: "CLR via C#" Troelson: "Pro C# 2008 and the .NET 3.5 Platform" Albahari & Albahari: "C# 3.0 in a Nutshell" Hejlsberg, Torgersen, Wiltamuth, & Golde: "The C# Programming Language,...