Can I use two phases of a three phase generator?
I'm a technician on a mission base in the Amazon. A few days ago we suffered a lighting strike to our electrical system when the generator was not running. The strike damaged one of our three step up transformers for our electrical distribution system. In a pinch could I run the generator only using two of it's three phases? Can I leave the third phase unloaded? I know people always say you can't but if you be sure to not exceed the rating of any one phase does it matter if the other phases are loaded or not?
The transformers are oil cooled 75KVA pole mountable units. The high voltage sides are wired delta. If I eliminated one of the transformers could I connect just two transformers together? Is there any way to limp along with just two step up transformers and energize just two legs of the distribution system? I'm assuming I could do like this:
ph1--(trans1)--ph2--(trans2)--ph3
Loads would go from 1 to 2 and 2 to 3. No load would be put on 1 to 3.
Would that work?
Thanks!
Greg
Thanks!
Greg
The transformers are oil cooled 75KVA pole mountable units. The high voltage sides are wired delta. If I eliminated one of the transformers could I connect just two transformers together? Is there any way to limp along with just two step up transformers and energize just two legs of the distribution system? I'm assuming I could do like this:
ph1--(trans1)--ph2--(trans2)--ph3
Loads would go from 1 to 2 and 2 to 3. No load would be put on 1 to 3.
Would that work?
Thanks!
Greg