Motor Overload Protection

This is a discussion on Motor Overload Protection within the Electrical & Electronics Engineering forums, part of the CE : Technical Discussions category; Hello I am using an electric hoist to pull a metal mandrel into a metal casing. Daily around 10 mandrels ...

  1. #1
    CE - Newbie
    Join Date
    30th July 2010
    I'm a crazy: electrical engineer

    Posts
    2

    Default Motor Overload Protection

    Hello

    I am using an electric hoist to pull a metal mandrel into a metal casing. Daily around 10 mandrels are pulled and pushed. Sometimes 1 out of hundred casing is under size which makes the mandrel tight to pull and makes the motor overloaded, hence the motor either breaks the wire or its winding damaged itself. What i want is an overload protection for the motor, i mean a kind of tripping mechanism which trips the motor mains line when the ampere goes more than say 10 ampere or 8 ampere wherever we set the value..

    So what apparatus is to be used for such kind of work?


    • Advertisements

      Advertisements
      CrazyEngineers has
      no influence on
      ads displayed by
      Google Adsense

        
       

  2. #2
    CE - Apprentice Muffy's Avatar
    Join Date
    26th May 2008
    I'm a crazy: Mechatronics engineer

    Location
    Chennai , India
    Posts
    41

    Default Re: Motor Overload Protection

    overload relays can be purchased form any switchgear dealer. They have 6 terminals , 3 for connecting phase wire from power, or contactor output, and the other 3 to motor. Other than these 6 , there are additional 2 terminals. This must be connected in series with the coil of the motor contactor. When theres an overload, the relay heats, breaks the NC connection between these two terminals. When this breaks the contactor coil circuit opens and the contactor switch opens.

    Overload relays are available in a wide range of amperages.

  3. #3
    CE - Newbie
    Join Date
    30th July 2010
    I'm a crazy: electrical engineer

    Posts
    2

    Default Re: Motor Overload Protection

    Thanks for the help.
    I installed a teknika brand Overcurrent relay which is appropriate. It has range of 1 to 5 amps(a rotating knob can be set) and also has a "time to tirp" setting(by a rotating knob). i have set it at 1 sec(its minimum) but i have realized that i need it to trip in .25 secs so as to protect the mechanical system that is attached to the motor. Where to find such sensitive relay in India?

  4. #4
    CE - Apprentice Muffy's Avatar
    Join Date
    26th May 2008
    I'm a crazy: Mechatronics engineer

    Location
    Chennai , India
    Posts
    41

    Default Re: Motor Overload Protection

    You will have to think of some other way to protect the mechanical system. with a very short trip time, your motor will fail to start, because the high starting current will trip it before it reaches the required rpm.

  5. #5
    CE - Regular Member
    CEoM August 2010
    aj_onduty's Avatar
    Join Date
    24th August 2010
    I'm a crazy: Electrical engineer

    Location
    India
    Posts
    148

    Default Re: Motor Overload Protection

    Kindly let me know the motor ratings.
    And, there are many relays which you can use, for example, the IDMT relay(Inverse definate Minimum Time lag relay). They adjust their tripping time according to the current flow in them. For motors, the initial starting current lasts for a little time. And this relay doesnt trip for that time, but if the starting current lasts for more than expected time, the relay detects it as an abnormal condition and it trips.The overload current is substantially higher compared to the starting current. So, when it flows through this relay, its tripping time is lowered and it trips in a very short time, thus saving your motor. This is usually used in large motors, and in large generator protection circuits. I believe this answer satisfies you.

+ Reply to Thread

Similar Threads

  1. Fault analysis of line protection and transformer protection
    By dileep k in forum Project Ideas & Seminar Topics
    Replies: 5
    Last Post: 26th July 2010, 07:15 PM
  2. what is a DRM protection ?
    By mohit007kumar00 in forum Computer Science & IT Engineering
    Replies: 1
    Last Post: 17th June 2010, 11:48 PM
  3. details of motor display of motor cycle
    By gsk_ssit in forum Mechanical & Civil Engineering
    Replies: 5
    Last Post: 14th April 2010, 12:38 AM
  4. Replies: 0
    Last Post: 2nd May 2009, 07:20 AM
  5. Another Take on an Empty Inbox [Email Overload]
    By CE-InFocus in forum CE - InFocus
    Replies: 0
    Last Post: 5th March 2009, 09:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts