Turn The Screws! Open your eyes, look in front, look at the back, look at any angle and you will see something that is an engineer's creation. Engineers have been making things possible that others could only imagine. It perfectly makes sense to have a common place for engineers from around the world where they can share ideas, innovate, & help each other. Engineers are eternal, with the younger at 62 & the youngest at 17, the CEan gang consists of working professionals, students, entrepreneurs, CEOs, professors, geeks & nerds. Need we say more? Click Here To Join The Gang! |
![]() |
| Sponsored links | |
|
|
|
|
CE - Apprentice
![]() ![]() |
Hey. This question was asked to me in my 3rd sem Lab viva..
Here goes the answer. KW shows the power consumed by a machine. Transformer is not a power consuming device, its a power transfer device. So the actual power consumed depends on the load applied to the secondary. As Deepak SR said the power consumed depends on the power factor of the secondary load. To calculate the KW rating, just multiply the KVA rating by the powerfactor if the seconday. So a 1000 KVA transformer when connected to a 0.7 pf secondary loaed used 1000*0.7= 700 KW power.. Got it..?